Wind Zones in ASCE7-05 Figure 6-2

Status
Not open for further replies.

hdn32

Structural
Sep 28, 2004
51
Let look at a rectangular building that is 40ft in width and 100ft in length. The calculated end zone length/width (2a) is 8ft.

In order to come up with base shear, I have been calculating interior zone length by subtracting the width or length of building by (2) end zones length (2x2a). Therefore, for 40ftx100ft building, the interior zone lengths will be 24ft and 84ft for the 40ft & 100ft wall/roof respectively.

ASCE7-05 Figure 6-2 seems to suggest that the interior width/length equal the width/length minus (1) end zone width/length.
Please let me know if my calculation is okay or not.
Thank you,

HDN.
 
Replies continue below

Recommended for you

Both ends are never the "end zones" simultaneously - so the overall base shear is based on just one end zone. However each corner must be taken as the reference corner in turn, so the frames on each end will see the effects of the end zone pressures, just not both ends at the same time.
 
Willis, thank you for your response.

I should have looked at wind zones similarly to what shown in ASCE7-05 figure 6-10.
Regards,
HDN
 