cmrdata

Structural
Oct 19, 2010
70
Design wind pressure tables in the ASCE 7-05 and FM Data Sheet 1-28 are quite comparable, if you take into account the additional importance factor of 1.15 adopted by FM for the cladding and components.
With the adoption of ASCE 7-10 in which wind load is based on ultimate load, I gather for certain buildings we might have do it twice:

1. Proceed with ASCE 7-10, with wind load as ultimate load, to satisfy the Building Code.
2. If the building is insured by FM, run a separate analysis/design with FM 1-28, with wind load as service load.
3. Compare the results from two designs above, and the more conservative one governs.

This sounds silly and I'm not sure what I miss here. I appreciate any comments you might have.
 
Replies continue below

Recommended for you

Why can't you determine the wind pressure using ASCE 7-10 (2012 IBC) ASD load combinations (0.6W) to get the wind pressure and compare this to FM?
 
Just had the same discussion in our office. Haven't found anywhere within FM documents on how they are incorporating the ASCE 7-10 wind changes.
But, I suspect you could get there a couple ways.
I would take the approach of assuming that FM's intent still applies. They bump up the code prescribed wind by a 1.15 importance factor and use Exposure C or worse.
And, FM is only concerned with components and cladding.
As wannabeSE suggests, using ASD , you could use ASCE7-10 to get wind pressures and factor down to ASD, but then you would need to apply the importance factor 1.15.
Or, if you are in a Category II building, you could use the ASCE 7-10 maps for category III and IV, which would include the 1.15 factor.

Until FM provides clarity, and I intend to ask an FM representative, it seems we end up specifying C&C loading that is, in our judgement, equivalent to their intent.
 