when is your service maxed? 2

Status
Not open for further replies.

syarn

Structural
Sep 10, 2008
27
if an engineer says
"...The electrical panel is 400amp/240v/1 ph
We currently have 335 amps connected to the panel before the addition of the dishwasher
The dishwasher will overload the panel..."
the dishwasher looks to have 50 rated amps, 60 amp minimum supply circuit conductor ampacity & 60 amp maximum overcurrent protective device per the spec sheet.
when I add 50 amps to 335 amps I get 385 amps how does that over load the panel?

steve yarnall

 
Replies continue below

Recommended for you

In the future ask the engineer your question. He should be happy to explain it. If he won't or seems bothered find a new one.

But to answer your question most authorities consider an installed load exceeding 80% of the equipment rating to be the maximum allowed. 80% of 400A = 320A

Keith Cress
kcress -
 
Of course you will probably have diversity which helps to take into account real-world conditions where it is unlikely that all loads will simultaneously draw rated power. It is not unusual to see boards with a total connected load of perhaps double the feeder capability in instances where diversity is low.
 
Did you do an actual load test on your electric panel or did you simply count the breakers and amperage on the breakers? 335 Amps is a huge load for a home. To really obtain the actual load on your 400 amp service, someone would need to do an actual load test with an amp probe on each phase.
 
djlozzi it is a commercial project (restaurant). the electrical engineer insisted the existing service had to be made larger and the client finally acknowledged...so the dishwasher was removed from the scope. thx u.

steve yarnall

 
For commercial kitchens, the NEC has very explicit load calculation requirements that need to be followed. Historically, restaurant kitchens have been a leading cause of fires, so the NEC developed some pretty strict requirements.

 
And what are the odds all breakers will be maxed out at any given time?? About ZERO. Or run the dishwasher at night.....

If in doubt - try it - you will find out soon enough!!
 
385A per phase consumption for an installation is considered huge.

What size of copper wiring that you are using at the moment?
 
385A per phase consumption for an installation is considered huge

Based on what? Everything is relative.
 
For a single phase installation of 400A panel, the incoming cable will be at least 240mm2. A normal practice will be using a 3 phase supply to balance out the load.
 
Normal practice where? 400A single phase is not at all uncommon.
 