Am not a S.E or a C.E. but an E.E, and I have a question that I would greatly appreciate being answered by knowledgeable Structural Engineers. Namely,in Chapter 19 of the UBC '97 under Seismic Requirements for Plain Concrete it states under Section 1922.10.3 that structural concrete members are not permitted in buildings in Seismic Zones 2,3 and 4, with the exception being "Non-structural slabs supported directly on the ground".
In sum, does this imply that all non-structural slabs supported on the ground,irrespective of the seismic zone do not have to be reinforced - even if they were - say 50 ft away from an active fault - where there have been 95 small to moderate earthquakes in the past 18 years ? If this is indeed the case, viz. that there is no code requirement for a nonstructural slab to ever be reinforced, no matter what the seismicity of the area and the proximity of a home to an active fault ,why is it that some structural engineers specify in their structural plans, that the interior slab of a home has to be reinforced, along with crack control joints ? Are they doing this solely because it is standard practice in the construction industry to reinforce a slab on grade and to install crack control joints, even though it costs several thousand dollars for the rebar or WWM ?
The other question that I have is : when you have a slab on grade with tall 4 ft bent "stem" rebar emanating from the perimeter and interior footings - before the concrete slab is poured- doesn't this tying of the slab to the footings - via this stem rebar -somehow make the slab "structural" such that the slab and the footings are now part of the lateral-force resisting system and hence via Section 1633 of the UBC '97 -provision must be made such that all building components in Seismic zones 2, 3, 4 must be designed to resist the effects of seismic forces ?
In sum,is one ever required by the UBC '97 code to reinforce a slab on grade ? And, if there is bent-over stem rebar coming up from the perimeter and interior footings, does this fact make the slab structural such that 1922.10.3 requires the slab to be reinforced? And, last - do the requirements of Chapter 16 - which take into consideration the seismic zone and the proximity of the site to active seismic sources take preference over what's stated in Section 1922.10.3 of the UBC '97 that non-structural slabs on grade in Seismic Zone 2,3,an4 do not have to be reinforced ?
As an E.E, who only took two C.E. courses - many, many years ago -I would greatly appreciate hearing a reply to my questions above.
Many thanks,
JRLF
In sum, does this imply that all non-structural slabs supported on the ground,irrespective of the seismic zone do not have to be reinforced - even if they were - say 50 ft away from an active fault - where there have been 95 small to moderate earthquakes in the past 18 years ? If this is indeed the case, viz. that there is no code requirement for a nonstructural slab to ever be reinforced, no matter what the seismicity of the area and the proximity of a home to an active fault ,why is it that some structural engineers specify in their structural plans, that the interior slab of a home has to be reinforced, along with crack control joints ? Are they doing this solely because it is standard practice in the construction industry to reinforce a slab on grade and to install crack control joints, even though it costs several thousand dollars for the rebar or WWM ?
The other question that I have is : when you have a slab on grade with tall 4 ft bent "stem" rebar emanating from the perimeter and interior footings - before the concrete slab is poured- doesn't this tying of the slab to the footings - via this stem rebar -somehow make the slab "structural" such that the slab and the footings are now part of the lateral-force resisting system and hence via Section 1633 of the UBC '97 -provision must be made such that all building components in Seismic zones 2, 3, 4 must be designed to resist the effects of seismic forces ?
In sum,is one ever required by the UBC '97 code to reinforce a slab on grade ? And, if there is bent-over stem rebar coming up from the perimeter and interior footings, does this fact make the slab structural such that 1922.10.3 requires the slab to be reinforced? And, last - do the requirements of Chapter 16 - which take into consideration the seismic zone and the proximity of the site to active seismic sources take preference over what's stated in Section 1922.10.3 of the UBC '97 that non-structural slabs on grade in Seismic Zone 2,3,an4 do not have to be reinforced ?
As an E.E, who only took two C.E. courses - many, many years ago -I would greatly appreciate hearing a reply to my questions above.
Many thanks,
JRLF