- Jul 18, 2003
- 8
Application: Centrifugal Pump (Variable Torque)
Motor: 200HP 1200RPM (FL RPM = 1185) 3/60/575V
447T TEFC
Some history: Motor/Pump operated approx. 4 years without problems with Direct on Line starting and running at full load RPM. Routine motor maintenance and observation had the motors running at approximate surface temperature of 60^C - 70^C.
Company decided to retrofit application with a Variable Frequency Drive for process control and operating cost savings. Motor rewound with Spike Resistant wire for application and VFD includes load reactors.
Immediate observation, with the motor running at 1000RPM, found motor surface temperature anywhere between 124^C and 143^C. With isolated area's of the motor at 170^C. (External blowers are keeping the motor operating)
VFD company validated the drive and gave it a clean bill of health. Power Quality Analysis found voltage transients at 2047.50V (In excess of NEMA but tolerable for spike wire in the short term - issue to be addressed)and THD of 10.153%, with maximum current total harmonic distortion of 14.49%.
Question: Do the above harmonic distortion value's fall within spec or not (IEEE 519-1992). And from the pools vast experience and suggestions any other observations would be welcome.
Cheers
Motor: 200HP 1200RPM (FL RPM = 1185) 3/60/575V
447T TEFC
Some history: Motor/Pump operated approx. 4 years without problems with Direct on Line starting and running at full load RPM. Routine motor maintenance and observation had the motors running at approximate surface temperature of 60^C - 70^C.
Company decided to retrofit application with a Variable Frequency Drive for process control and operating cost savings. Motor rewound with Spike Resistant wire for application and VFD includes load reactors.
Immediate observation, with the motor running at 1000RPM, found motor surface temperature anywhere between 124^C and 143^C. With isolated area's of the motor at 170^C. (External blowers are keeping the motor operating)
VFD company validated the drive and gave it a clean bill of health. Power Quality Analysis found voltage transients at 2047.50V (In excess of NEMA but tolerable for spike wire in the short term - issue to be addressed)and THD of 10.153%, with maximum current total harmonic distortion of 14.49%.
Question: Do the above harmonic distortion value's fall within spec or not (IEEE 519-1992). And from the pools vast experience and suggestions any other observations would be welcome.
Cheers