Vessels Manways 2

Inchtain

Petroleum
Feb 21, 2021
151
According to the relevant standards and codes, is there a minimum recommended diameter for a manway e.g. 24 inches." , so that the entry into the vessel can be refused due to safety reasons.

Is that also valid for entering pressure vessels for inspection during total shutdown of the Plant?

Regards,
 
Replies continue below

Recommended for you

Please be clear: what kind of safety reasons?
 
UG-46 is very clear what minimum size of manway or inspection hole must have. As long as you meet that criteria, your entering of the manhole is at your own risk, no one can stop you. Any concern, you'd better hire a hole watch to recue you in time. However, making sure well ventilation and no residual gas, liquid that can harm you.
The minimum size I have done is 18" ID because owner wanted to save cost, and as big as more than 100" ID for special internals to get in and out.
Nowadays, since American are getting bigger, 30" could be the trend.
 
One person must remain outside while you are inside. Both people must maintain eye contact at all times.
 
Company, local or national regulations should have requirements for access and confined space work. Our national standards cover wide a range of requirements including required training and rescue provisions.

Regarding manways, DN750 is often the minimum plant owners now require.
 
12" x 16" elliptical manway or 16" diameter is minimum per Sec. VIII.
Provincial regulations will usually coincide with these minimum sizes. Site specs may be way different.
 