bjenks
Electrical
- Jul 14, 2006
- 68
In the IEEE Red book, when you are calculating the utility Zpu they just use the simple formula: (KVAbase)/(KVAsource) which is a unit less number.
Thus for a base of 100MVA and a fault MVA of 400 you would get Zpu=100/400=.25pu.
I don't understand the math behind that simple formula as I would think the formula would be based on kV*kV/MVA. So with the utility at 69kV the Zbase would be69*69/100= 47.61 which would then be converted to Zpu somehow or other. I understand all the other pu calculation, just not the utility.
Thus for a base of 100MVA and a fault MVA of 400 you would get Zpu=100/400=.25pu.
I don't understand the math behind that simple formula as I would think the formula would be based on kV*kV/MVA. So with the utility at 69kV the Zbase would be69*69/100= 47.61 which would then be converted to Zpu somehow or other. I understand all the other pu calculation, just not the utility.