Electrical
- Jul 31, 2003
- 100
A customer has an unusual distribution system that may be ill-advised but has been operating for some time. The utility services the site with a 4.16kV solid grounded source. The customer takes delivery through a 2000A breaker and then uses a delta delta 7500KVA transformer to step up the voltage to a 12.47kV ungrounded open overhead line distribution system. Some recent equipment additions connected on drops off the overhead line allowed one or more ground faults to occur on the 12.47kV system. Very little physical damage was done before the 4.16kV breaker tripped with a 50N (1600A primary pickup) indication. Can anyone offer an explanation of how any fault on the 12.47kV side could appear as a ground fault on the "other" side of a delta delta connection? The 50N relay is connected in the residual of three 2000/5 CTs with an equivalent 4A secondary pickup.