racobb
Electrical
- Feb 23, 2009
- 327
Looking forward to input!
In summer 2008 we commissioned a 20/27/33 MVA, 115-25 kV, Delta-Wye substation transformer. Subsequently we have had 3 differential trip events on the unit and have yet to determine the cause. Except for thes ethree events the transformer has otherwise been in service, we have had faults on circuits with no differential issues.
First event - Fall of 2009
Don't remember the type of trip. Transformer mfg came in and found several of the stud connections on the feed through bushings very loose. Loose such that some of the ring terminals were not even hand tightened! Some burning on one feed through and it was replaced.
Tests
DGA for the oil
TTR for the transformer
Ratio for the CT's
Review of the diff settings
All tests were acceptable and the unit was returned to service with the thought that CT connections were the problem.
Second event - Fall of 2010
Restrained Diff trip on B phase and lockout of high side circuit switcher. Again mfg was called in. Found all CT connections tight on feed throughs but one exhibited severe burning and was replaced.
Tests Again
DGA for oil
TTR for the transformer
Ratio for the CT's
Review of diff settings
Review wiring for grounds/proper connections, etc.
Diff relay sent to mfg for complete testing....found ok
Diff relay mfg reviewed settings and found no issue
Third event - Fall of 2012
Another restrained trip on phase B and lockout. Diff trip and lockout of the high side circuit switcher for fault on distribution circuit. Owner opened all distribution breakers, reset lockout relay, and closed circuit switcher thus re-energizing transformer! YES a definite NO-NO! Then closed one un-faulted circuit and diff tripped and locked out station. This trip is assumed to be from inrush on a circuit that had approx. 50 to 75 amps of steady state load. Mfg called in again. No CT or feed through issues found.
Test again
DGA for oil
TTR for transformer
Ratio for CT's
Review wiring and settings for diff relay and again checked for inadvertent grounds
Diff relay mfg had 2 engineers review settings....no issues found
Excitation test of CT's this time....ok so far
Awaiting results of oil tests.
We have approx 5,000 amps of available fault duty at the transformer low side.
Differential relay is a Basler BE1-87T with no memory so event history is not available.
High side Ct's are 600/5 MRBCT set on 200 amp tap
Low side Ct's are 1200/5 MRBCT det on 1000 amp tap
Any Ideas....additional tests? I know there are more tests we could do for the health of the unit, but given the issues we have found with the Ct's over time, we have been concentrating on that. Short of shutting down the station in the months of Sept and Oct each year, don't know what else to do. If it is a false trip, it is the first one I have ever experienced.
Would love to get some input!
Thanks
Alan
In summer 2008 we commissioned a 20/27/33 MVA, 115-25 kV, Delta-Wye substation transformer. Subsequently we have had 3 differential trip events on the unit and have yet to determine the cause. Except for thes ethree events the transformer has otherwise been in service, we have had faults on circuits with no differential issues.
First event - Fall of 2009
Don't remember the type of trip. Transformer mfg came in and found several of the stud connections on the feed through bushings very loose. Loose such that some of the ring terminals were not even hand tightened! Some burning on one feed through and it was replaced.
Tests
DGA for the oil
TTR for the transformer
Ratio for the CT's
Review of the diff settings
All tests were acceptable and the unit was returned to service with the thought that CT connections were the problem.
Second event - Fall of 2010
Restrained Diff trip on B phase and lockout of high side circuit switcher. Again mfg was called in. Found all CT connections tight on feed throughs but one exhibited severe burning and was replaced.
Tests Again
DGA for oil
TTR for the transformer
Ratio for the CT's
Review of diff settings
Review wiring for grounds/proper connections, etc.
Diff relay sent to mfg for complete testing....found ok
Diff relay mfg reviewed settings and found no issue
Third event - Fall of 2012
Another restrained trip on phase B and lockout. Diff trip and lockout of the high side circuit switcher for fault on distribution circuit. Owner opened all distribution breakers, reset lockout relay, and closed circuit switcher thus re-energizing transformer! YES a definite NO-NO! Then closed one un-faulted circuit and diff tripped and locked out station. This trip is assumed to be from inrush on a circuit that had approx. 50 to 75 amps of steady state load. Mfg called in again. No CT or feed through issues found.
Test again
DGA for oil
TTR for transformer
Ratio for CT's
Review wiring and settings for diff relay and again checked for inadvertent grounds
Diff relay mfg had 2 engineers review settings....no issues found
Excitation test of CT's this time....ok so far
Awaiting results of oil tests.
We have approx 5,000 amps of available fault duty at the transformer low side.
Differential relay is a Basler BE1-87T with no memory so event history is not available.
High side Ct's are 600/5 MRBCT set on 200 amp tap
Low side Ct's are 1200/5 MRBCT det on 1000 amp tap
Any Ideas....additional tests? I know there are more tests we could do for the health of the unit, but given the issues we have found with the Ct's over time, we have been concentrating on that. Short of shutting down the station in the months of Sept and Oct each year, don't know what else to do. If it is a false trip, it is the first one I have ever experienced.
Would love to get some input!
Thanks
Alan