Hello everybody,
When you have a large industrial plant extended over a large area there are typically several electrical rooms, each one has its own grounding grid, all of the buildings have a ground ring and the main substation has another grounding grid and all of these elements are joined together.
IEEE std 80, states that in order to size the conductor to be buried the shorcircuit current on the secondary side of the main transformer (at the main substation) should be considered but, to determine GPR, touch and step voltages only primary side shorcircuit current of the main transformer has to be considered.
However, when you have a large industrial system and all the grounding grids, rings are joined together, we surely have low voltage transformers (460-480 V) wye grounded which shortcircuit current has a very high magnitude.
Then, my questions are:
Will these low voltage side shortcircuit currents have to be considered to size the conductor to be buried?
Do we need to determine step and touch voltages in low voltage electrical rooms with the corresponding shortcircuit current?
I ask this, because, doing the evaluations with low voltage side shortcircuit currents the size of the conductor, step and touch voltages have higher magnitudes and I do not know if my previous description is taken into account to design the grounding grids of industrial systems or is not.
Any help or comment will be appreciated!
When you have a large industrial plant extended over a large area there are typically several electrical rooms, each one has its own grounding grid, all of the buildings have a ground ring and the main substation has another grounding grid and all of these elements are joined together.
IEEE std 80, states that in order to size the conductor to be buried the shorcircuit current on the secondary side of the main transformer (at the main substation) should be considered but, to determine GPR, touch and step voltages only primary side shorcircuit current of the main transformer has to be considered.
However, when you have a large industrial system and all the grounding grids, rings are joined together, we surely have low voltage transformers (460-480 V) wye grounded which shortcircuit current has a very high magnitude.
Then, my questions are:
Will these low voltage side shortcircuit currents have to be considered to size the conductor to be buried?
Do we need to determine step and touch voltages in low voltage electrical rooms with the corresponding shortcircuit current?
I ask this, because, doing the evaluations with low voltage side shortcircuit currents the size of the conductor, step and touch voltages have higher magnitudes and I do not know if my previous description is taken into account to design the grounding grids of industrial systems or is not.
Any help or comment will be appreciated!