Sanchez01
Electrical
- Oct 13, 2010
- 18
We have to calculate the total relay time (tripping delay) for a 115 kV Breaker for fault analysis.
Let’s say primary lead differential relays operate a lockout relay which in turn trips another WL-1 relay for breaker trip.
The results (test conducted a decade ago) we have is as follows:
• A phase A Phase 3.2 cycles @ 160 amps 5.5 cycles @ 600 volts
• B Phase 3.17 cycles @ 160 amps 4.70 cycles @ 600 volts
• C Phase 3.8 cycles @ 160 amps 4.81 cycles @ 600 volts
Question is, do I pick the phase with longest cycle? If yes, since this is 115 kV breaker, do you go with 160 A or 600 V? We are looking at a fault of about 65 kA value.
This in turn trips WL-1 relay which takes about 2 cycles. This means, our total relay time is X + 2, where X is the answer to my above question.
Right?
Answer will be appreciated.