I am seeking clarification about the zero sequence network connection for the following three-winding transformer:
High: Wye-Grounded (connected to utility source)
Nominal KVA: 16000
Rated Voltage: 34400
Medium: Wye-Grounded
Nominal KVA: 16000
Rated Voltage: 17200
Low: Delta
Nominal KVA: 2400
Rated Voltage: 2400
For a SLG fault on the bus directly upstream of the High side of this transformer, my understanding is that the ground fault current is affected by the parallel connection of the utility and transformer High-to-Low zero sequence networks. My hand calculation for this SLG fault is not agreeing with the results produced by SKM PowerTools. Is the parallel connection between the utility and transformer different than I am assuming?
Thanks in advance.
High: Wye-Grounded (connected to utility source)
Nominal KVA: 16000
Rated Voltage: 34400
Medium: Wye-Grounded
Nominal KVA: 16000
Rated Voltage: 17200
Low: Delta
Nominal KVA: 2400
Rated Voltage: 2400
For a SLG fault on the bus directly upstream of the High side of this transformer, my understanding is that the ground fault current is affected by the parallel connection of the utility and transformer High-to-Low zero sequence networks. My hand calculation for this SLG fault is not agreeing with the results produced by SKM PowerTools. Is the parallel connection between the utility and transformer different than I am assuming?