Hi all,
I have 5 VFDs each with manufacturer test reported %THD content of 4.3% at 88% loading.
IEEE std 519 requires total harmonic distortion of 8% and I am getting 8.6% THD at 80% VFD loading and 11% at 100% loading at the 600V MCC bus where all these VFDs are connected and this is the only MCC bus I can connect them.
The upstream supply transformer primary is less than 3% THD.
Is it applicable to apply TOTAL 8% THD criteria to a bus where all my VFDs are connected?
Or can I justify if the resulting voltage and current harmonics total are within the voltage and current rating of the bus and main cables?
Regards