Dear all,
I have to control the outlet temperature of natural gas process fluid, which flows in the tube side of a vertical beu HEX.
At the shell side steam is condensates. By modulate steam mass flow with a throttling control valve you can control natural gas temperature. Classic temperature control method at HEX.
The problem is that in any case condensation pressure is arises from the heat and mass balance into the HEX. At very low load pressure will decreased and it may reach even 1barg. Then it is difficult for condensate to be transmitted in to the atmospheric flash tank.
In cases that a condenser shall operates at a variable loads with a significant range then HEX pressure will varies a lot. You need then a pressure control system.
The key is to install (and not the only solution) a control valve at condensation line in order to create a level at low loads and reducing thus saturation area. Then HEX pressure will increased.
The question is can you achieve with pressure control and temperature control i.e. one control valve in condensate side can handle HEX pressure and natural gas temperature ?
Or you need two control valves, one for temperature and the other for pressure control ?
Please note here that pressure and level control has the same meaning
I have to control the outlet temperature of natural gas process fluid, which flows in the tube side of a vertical beu HEX.
At the shell side steam is condensates. By modulate steam mass flow with a throttling control valve you can control natural gas temperature. Classic temperature control method at HEX.
The problem is that in any case condensation pressure is arises from the heat and mass balance into the HEX. At very low load pressure will decreased and it may reach even 1barg. Then it is difficult for condensate to be transmitted in to the atmospheric flash tank.
In cases that a condenser shall operates at a variable loads with a significant range then HEX pressure will varies a lot. You need then a pressure control system.
The key is to install (and not the only solution) a control valve at condensation line in order to create a level at low loads and reducing thus saturation area. Then HEX pressure will increased.
The question is can you achieve with pressure control and temperature control i.e. one control valve in condensate side can handle HEX pressure and natural gas temperature ?
Or you need two control valves, one for temperature and the other for pressure control ?
Please note here that pressure and level control has the same meaning