cbark
Electrical
- Aug 5, 2011
- 11
We are installing a new 2500 kVA, 13,800-480Y/277 V transformer (solidly grounded) that will feed a new 480 V, 3000 A lineup of switchgear (3 phase, 4 wire). The transformer is located outside the building and will be cable connected to the new switchgear inside the building via underground conduit. The secondary main breaker is in the switchgear and it is about a 50’ run from the transformer secondary to the switchgear. We are going to run 8 parallel sets of 500 kcmil cables (3 phase and 1 neutral). The question I have is about where the system should be connected to ground. Should the neutral be connected to the system ground at the transformer X0 bushing or in the switchgear? Do ground/bonding conductors need to be run from the transformer to the switchgear along with the phase and neutral conductors?