System Grounding Question

Status
Not open for further replies.

SparkOmatix

Electrical
Oct 26, 2010
29
We have a compressor/meter-station site where we have grounded everything together via copper wire underground and grounding rods. There is one portion (meter skid) where they will install isolation kits at the incoming and outgoing flanges...ultimately isolating this portion from everything else. They wish to ground this skid separately/independently with rods placed into the ground near the skid. There is shielded CAT-6 going to the meter from a device that is part of the larger grounded system. Is this a bad idea (different potential)? Can a ground loop occur? Your thoughts/comments are greatly appreciated!
 
Replies continue below

Recommended for you

In general this is a bad idea and possibly a violation of the NEC. Everything should be bonded together. It is a safety concern.
 
After the independent ground rods are installed, the code requires a jumper to the main grounding grid. There is a potential for excess touch and step voltages to develop on the skid if it is not connected to the main ground grid.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 