I have a 13.2kV double ended switch gear, with a primary 13.2kV feed from the utility. At the other end a backup feed from a generator.
I am seeing what I believe to be a switching transient when I switch the loads to and from the generator. The generator is 2000 kW 480V wye and stepped up to 13.3kV delta. The generator breaker is on the 480V side. It is an air breaker - Cutler Hammer SPB100 series rated for 4,000 Amps. The generator breaker is interlocked with the incoming 13.2kV motorized air break switch. The transfer from generator to utility is open transition. I am seeing 2 distinct problems that both manifest themselves as excessive arcing across the arcing contacts on the generator breaker.
Scenario #1: plant is running on generator and the sequence to transfer to utility is initiated, when the generator breaker breaks the load we have seen excessive arcing across the arcing contacts on two phases of the generator breaker.
Scenario #2: plant is running on generator and the sequence to transfer to utility is initiated, the generator breaker breaks the load, and 3 seconds later the incoming 13.2 kV air break switch is closed. At that point in time we have seen arcing across the OPEN arcing contacts in the generator breaker.
The loads are mostly inductive, but there is a 1 mile of 13.2kV underground cable feeding the several unit substations.
I have been looking at surge supressor/arrestor circuits, but I do not know where to apply them, at the generator breaker? on the 13.2k V side of the step up transfomer. I alos have questions on sizing.
Am I on th right track? any sugestions welcomed.
I am seeing what I believe to be a switching transient when I switch the loads to and from the generator. The generator is 2000 kW 480V wye and stepped up to 13.3kV delta. The generator breaker is on the 480V side. It is an air breaker - Cutler Hammer SPB100 series rated for 4,000 Amps. The generator breaker is interlocked with the incoming 13.2kV motorized air break switch. The transfer from generator to utility is open transition. I am seeing 2 distinct problems that both manifest themselves as excessive arcing across the arcing contacts on the generator breaker.
Scenario #1: plant is running on generator and the sequence to transfer to utility is initiated, when the generator breaker breaks the load we have seen excessive arcing across the arcing contacts on two phases of the generator breaker.
Scenario #2: plant is running on generator and the sequence to transfer to utility is initiated, the generator breaker breaks the load, and 3 seconds later the incoming 13.2 kV air break switch is closed. At that point in time we have seen arcing across the OPEN arcing contacts in the generator breaker.
The loads are mostly inductive, but there is a 1 mile of 13.2kV underground cable feeding the several unit substations.
I have been looking at surge supressor/arrestor circuits, but I do not know where to apply them, at the generator breaker? on the 13.2k V side of the step up transfomer. I alos have questions on sizing.
Am I on th right track? any sugestions welcomed.