Anybody have good experience slotting switchgear enclosure walls to eliminate heating caused by eddy currents?
We have a high amperage, medium voltage section, with only one small area of cubicle sidewall overheating, proximate to where nearest vertical bus joins horizontal main bus.
Heating is localized to area where apparently the magnetic field from vertical bus interacts with magnetic fields of horizontal bus.
It is thought that a slot cut in the sidewall may extend circulating current length, to dissipate heating effects over greater area, resulting in lower peak temperature.
The added slot is anticipated to be approx 12” long, and will be covered with insulated non magnetic panel of stainless steel to maintain section integrity.
A vertical slot (parallel to bus) will be difficult/ impossible to cut to panel edge, and concern is that such a slot may cause current CONCENTRATION in remaining small strip of enclosure metal, aggravating the problem. Horizontal slot, cut thru area of heating will result in large uncut panels beyond, so concentrated heating is not a concern, however, concern is whether this will have any effect.
We have a high amperage, medium voltage section, with only one small area of cubicle sidewall overheating, proximate to where nearest vertical bus joins horizontal main bus.
Heating is localized to area where apparently the magnetic field from vertical bus interacts with magnetic fields of horizontal bus.
It is thought that a slot cut in the sidewall may extend circulating current length, to dissipate heating effects over greater area, resulting in lower peak temperature.
The added slot is anticipated to be approx 12” long, and will be covered with insulated non magnetic panel of stainless steel to maintain section integrity.
A vertical slot (parallel to bus) will be difficult/ impossible to cut to panel edge, and concern is that such a slot may cause current CONCENTRATION in remaining small strip of enclosure metal, aggravating the problem. Horizontal slot, cut thru area of heating will result in large uncut panels beyond, so concentrated heating is not a concern, however, concern is whether this will have any effect.