What is the result of excessive pressure drop in the suction line? I typically have seen suction line design for 1-2 psig drop.
We have a bus AC system measuring 25-35 psig drop from evap out to compressor suction. The line sizes are obviously too small and that is being changed. However, I received reports the oil site glass in the compressor is "foaming". Can excessive pressure loss and or excessive superheat contribute to this phenomenon?
We have a bus AC system measuring 25-35 psig drop from evap out to compressor suction. The line sizes are obviously too small and that is being changed. However, I received reports the oil site glass in the compressor is "foaming". Can excessive pressure loss and or excessive superheat contribute to this phenomenon?