RSChinn
Electrical
- Nov 19, 2007
- 38
We just received a new substation switchgear and the control wiring to the feeder breakers (and generally everywhere) is #14awg. The control circuit is protected by a 30A breaker (per feeder breaker mfgr GE). The switchgear mfgr claims he is only obligated to follow ANSI C37.20.2 which says size the wire for the anticipated steady state load and overcurrent is not a consideration. However, our utility follows NESC and para.161.A says that a conductor and its insulation must be protected from overheating by overcurrent, alarms, indication or tripping devices. A #14awg wire cannot be protected by a 30A breaker. Question 1: Is there a grey area here?
Question 2: If the switchgear manufacturer is OK to do this, are we OK to install new circuitry into the switchgear using his requirements only? (We were going to add a completely new annunciator with #18awg wiring and protect it with a 20A panel breaker claiming the switchgear mfgr's logic. I would like to see us protect it with a 10A breaker instead. Our #18awg 90 degree C wire can handle 14A.)
Question 2: If the switchgear manufacturer is OK to do this, are we OK to install new circuitry into the switchgear using his requirements only? (We were going to add a completely new annunciator with #18awg wiring and protect it with a 20A panel breaker claiming the switchgear mfgr's logic. I would like to see us protect it with a 10A breaker instead. Our #18awg 90 degree C wire can handle 14A.)