edison123
Electrical
- Oct 23, 2002
- 4,508
Telemacanique Altivar 71 VFD driving a 440 V, 100 HP, 60 Hz, 350 RPM vertical motor (vertical machining centre)
Parameters set in VFD:
Motor voltage - 440V
Motor current – 169A
Motor KW – 75
Motor frequency – 60Hz
Motor rpm - 350
Running Frequency - 23.3 Hz (136 RPM)
Output as measured by VFD metering: Voltage-169 V, Current -98.5A, Speed-136 rpm & Frequency-23.3Hz. (Power & power factor could not be measured)
Input as measured by external Schneider Power meter ION6200/0.5 class accuracy : Voltage-424V, Current-12.6A, 11.8A, 7.4A , Power Factor-0.93 & Power - 5.2 KW
Why such a wide unbalanced VFD input currents ?
Why the power of 5.2 KW does not seem to tally with the average current of 10.6 A and PF of 0.93 and voltage of 424 V ?
Why the VFD does not show power and pf on the motor (VFD output) side ?
BTW, the no-load current of the motor is high at around 70% of FLC but that is normal for such a low speed motor.
Parameters set in VFD:
Motor voltage - 440V
Motor current – 169A
Motor KW – 75
Motor frequency – 60Hz
Motor rpm - 350
Running Frequency - 23.3 Hz (136 RPM)
Output as measured by VFD metering: Voltage-169 V, Current -98.5A, Speed-136 rpm & Frequency-23.3Hz. (Power & power factor could not be measured)
Input as measured by external Schneider Power meter ION6200/0.5 class accuracy : Voltage-424V, Current-12.6A, 11.8A, 7.4A , Power Factor-0.93 & Power - 5.2 KW
Why such a wide unbalanced VFD input currents ?
Why the power of 5.2 KW does not seem to tally with the average current of 10.6 A and PF of 0.93 and voltage of 424 V ?
Why the VFD does not show power and pf on the motor (VFD output) side ?
BTW, the no-load current of the motor is high at around 70% of FLC but that is normal for such a low speed motor.