The National Standard Plumbing Code requires main roof drains to be sized for 1 hour 100 year storm. The secondary drainage must be sized per the 15 minute 100 year storm, which is about three times as much flow.
If there is an areawell with drains discharging to a pump in the basement, should the pump be sized based on the 1 hour storm or the 15 minute storm? In my case, the 1 hour storm is 130 gpm and the 15 minute storm is 310 gpm.