Sorry its a bit long, trying to answer all the questions I would be asking... I am not the EOR, just designing the steel shear connections.
-Standard AISC steel shear connection, single shear plate bolted to the web of a supported beam and welded to an embed plate support in a concrete tilt-panel.
-Existing building, finishes up and this will have to be a weekend job probably.
-Third floor beam, temp shoring and jacking pretty much out of the question.
-Dead loads and some live loads (obviously more or less depending on the time of day) in place, building occupied.
-It was determined the existing shear connection was about one bolt short or about 6 kip.
1. Does AISC allow you to add the strength of an additional weld from the shear plate to the web of the now-bolted beam?
2. To maintain a connection that allows some rotation to maintain a pin-pin assumption, the weld could be placed only near the bottom. I'm winging this email so pardon my mechanics of materials memory, can't remember where exactly the least amount of movement at the end of the beam would occur..
3. The bolts should be in full bearing condition and local
deformations for the most part should have taken place inside the connection, correct? I know it depends on % of dead and live load, size of the holes, etc.
4. Alternatively, what about adding a shear plate to the opposite side of the web and turn this into a double shear connection? They could take the nuts off of the existing connection, slide another shear plate on, weld it to the embed plate, then tighten up the nuts....
The problem I see with that is making sure the bolts are bearing on the new shear plate once it is welded up there , so it is not just there for peace of mind. I am worried the connection would have to yield slightly to begin bearing on the new plate, but maybe that is acceptable? Would I have to use a slip critical connection to ensure load transfer?
5. Other options include possibly a angle seat below the beam, or drilling the holes larger and replacing the bolts with 7/8" dia.
Any references to AISC or other advice would be greatly appreciated.
Thanks in advance,
Andrew Kester, PE
Florida
-Standard AISC steel shear connection, single shear plate bolted to the web of a supported beam and welded to an embed plate support in a concrete tilt-panel.
-Existing building, finishes up and this will have to be a weekend job probably.
-Third floor beam, temp shoring and jacking pretty much out of the question.
-Dead loads and some live loads (obviously more or less depending on the time of day) in place, building occupied.
-It was determined the existing shear connection was about one bolt short or about 6 kip.
1. Does AISC allow you to add the strength of an additional weld from the shear plate to the web of the now-bolted beam?
2. To maintain a connection that allows some rotation to maintain a pin-pin assumption, the weld could be placed only near the bottom. I'm winging this email so pardon my mechanics of materials memory, can't remember where exactly the least amount of movement at the end of the beam would occur..
3. The bolts should be in full bearing condition and local
deformations for the most part should have taken place inside the connection, correct? I know it depends on % of dead and live load, size of the holes, etc.
4. Alternatively, what about adding a shear plate to the opposite side of the web and turn this into a double shear connection? They could take the nuts off of the existing connection, slide another shear plate on, weld it to the embed plate, then tighten up the nuts....
The problem I see with that is making sure the bolts are bearing on the new shear plate once it is welded up there , so it is not just there for peace of mind. I am worried the connection would have to yield slightly to begin bearing on the new plate, but maybe that is acceptable? Would I have to use a slip critical connection to ensure load transfer?
5. Other options include possibly a angle seat below the beam, or drilling the holes larger and replacing the bolts with 7/8" dia.
Any references to AISC or other advice would be greatly appreciated.
Thanks in advance,