What is the best way to control low-pressure steam (3.5 barG) flow to the air preheaters or steam reboilers channel head? Is it correct to install FRC on the steam inlet side or condensate outlet side?
If control valve is on the steam inlet side, the pressure of steam condensation may be changed (which changes temperature of condensation) and thus allowing operators to control heat input. If control valve is on the condensate outlet side, the way of changing heat input to the preheater is achieved by varying condensate level, i.e. varying condensing/subcooling surface area ratio.
What is the preffered method when using low-pressure steam in such services?
I have one particular control scheme on my mind, it looks to me rather interesting and flexible when using low-pressure steam for heating purposes ("Lesson learned by watching home radiators").
Heat input is controlled by varying condensate level in preheater's channel head, but not directly - there's a separate condensate pot, connected to the lower part of channel head (below pass-partition baffle) by pressure-equalizing line. Since both are at the same pressure, the level in the pot corresponds to the level in the channel head. By varying condensing/subcooling heat exchange surface area ratio, the overall heat duty is being changed. Another good part of such arrangement is prevention of CO2 or air pocketing in the channel head (which would promote CO2 corrosion and reduced heat duty by lowering steam partial pressure).
Additional protection is "level override": LC on the condensate pot assumes control at high & low level values, in order to prevent excessive condensate backup or blowing out the condensate seal. Steam line, as usually, has an ordinary gate valve which could be used anyway for changing steam condensing temperature (by changing pressure in the channel head), but it's not of much importance in low-pressure steam services, because there's too little space for varying condensing pressure between the steam header and condensate header pressure.
Again, I think this applies only for low-pressure steam services.
Please comment.
If control valve is on the steam inlet side, the pressure of steam condensation may be changed (which changes temperature of condensation) and thus allowing operators to control heat input. If control valve is on the condensate outlet side, the way of changing heat input to the preheater is achieved by varying condensate level, i.e. varying condensing/subcooling surface area ratio.
What is the preffered method when using low-pressure steam in such services?
I have one particular control scheme on my mind, it looks to me rather interesting and flexible when using low-pressure steam for heating purposes ("Lesson learned by watching home radiators").
Heat input is controlled by varying condensate level in preheater's channel head, but not directly - there's a separate condensate pot, connected to the lower part of channel head (below pass-partition baffle) by pressure-equalizing line. Since both are at the same pressure, the level in the pot corresponds to the level in the channel head. By varying condensing/subcooling heat exchange surface area ratio, the overall heat duty is being changed. Another good part of such arrangement is prevention of CO2 or air pocketing in the channel head (which would promote CO2 corrosion and reduced heat duty by lowering steam partial pressure).
Additional protection is "level override": LC on the condensate pot assumes control at high & low level values, in order to prevent excessive condensate backup or blowing out the condensate seal. Steam line, as usually, has an ordinary gate valve which could be used anyway for changing steam condensing temperature (by changing pressure in the channel head), but it's not of much importance in low-pressure steam services, because there's too little space for varying condensing pressure between the steam header and condensate header pressure.
Again, I think this applies only for low-pressure steam services.
Please comment.