wthall
Electrical
- Sep 18, 2002
- 10
My client wants a back-up generator for his 125HP, 480V, 3phase fire pump motor. The fire pump controller is an 'across-the-line' starter type.
I have gone through some sizing software provided by generator manufacturers and I came up with a 200kW unit. The factory guy tells me I need a 500kW unit because of
NFPA 20 6-2
"Power Source(s). Power shall be supplied to the electric motor-driven fire pump by a reliable source or two or more approved independent sources, all of which shall make compliance with Section 6-4 possible."
NFPA 20 6-4
"Voltage Drop. The voltage at the controller line terminals shall not drop more than 15 percent below normal (controller-rated voltage) under motor-starting conditions. The voltage at the motor terminals shall not drop more than 5 percent below the voltage rating of the motor when the motor is operating at 115 percent of the full-load current rating of the motor."
Then I look at NFPA 20 6-6 'On-Site Power Generator Systems'
6-6.1
Where on-site generator systems are used to supply power to fire pump motors to meet the requirements of 6-2.3, they shall be of sufficient capacity to allow normal starting and running of the motor(s) driving the fire pump(s) while supplying all other simultaneously operated load(s). A tap ahead of the on-site generator disconnecting means shall not be required.
6-6.2*
These power sources shall comply with Section 6-4 and shall meet the requirements of Level 1, Type 10, Class X systems of NFPA 110, Standard for Emergency and Standby Power Systems. The fuel supply capacity shall be sufficient to provide 8 hours of fire pump operation at 100 percent of the rated pump capacity in addition to the supply required for other demands."
NFPA 110
2-2.2 Type.
Type defines the maximum time, in seconds, that the EPSS will permit the load terminals of the transfer switch to be without acceptable electrical power.
Type 10: 10 seconds
I'm confused about the 15% vs. the ten seconds. Am I going to have to get this huge generator?
I have gone through some sizing software provided by generator manufacturers and I came up with a 200kW unit. The factory guy tells me I need a 500kW unit because of
NFPA 20 6-2
"Power Source(s). Power shall be supplied to the electric motor-driven fire pump by a reliable source or two or more approved independent sources, all of which shall make compliance with Section 6-4 possible."
NFPA 20 6-4
"Voltage Drop. The voltage at the controller line terminals shall not drop more than 15 percent below normal (controller-rated voltage) under motor-starting conditions. The voltage at the motor terminals shall not drop more than 5 percent below the voltage rating of the motor when the motor is operating at 115 percent of the full-load current rating of the motor."
Then I look at NFPA 20 6-6 'On-Site Power Generator Systems'
6-6.1
Where on-site generator systems are used to supply power to fire pump motors to meet the requirements of 6-2.3, they shall be of sufficient capacity to allow normal starting and running of the motor(s) driving the fire pump(s) while supplying all other simultaneously operated load(s). A tap ahead of the on-site generator disconnecting means shall not be required.
6-6.2*
These power sources shall comply with Section 6-4 and shall meet the requirements of Level 1, Type 10, Class X systems of NFPA 110, Standard for Emergency and Standby Power Systems. The fuel supply capacity shall be sufficient to provide 8 hours of fire pump operation at 100 percent of the rated pump capacity in addition to the supply required for other demands."
NFPA 110
2-2.2 Type.
Type defines the maximum time, in seconds, that the EPSS will permit the load terminals of the transfer switch to be without acceptable electrical power.
Type 10: 10 seconds
I'm confused about the 15% vs. the ten seconds. Am I going to have to get this huge generator?