Smoke detector spacing with low height ceiling and beams.
DavidCR
359
Hello.
A question on smoke detector spacing/location.
Case:
Intermediate floor with low ceiling.
Ceiling height: H=2m (6.7´)
Beam height: h=0.38m (15")
Beam distance: L=1m (3.3´)
For smoke detectors: since h>0.1H, and L>0.4*H >them each beam space is a pocket so I need a @#%& lot of detectors.
On "beam reduction rules" as per NFP72, or an manufacturers rules is there a consideration for low ceilings?.
Do reduction rules on detector spacing apply the same if the ceiling is relatively low?
What kind of business are they going in??
Why are they required?
Client requirement. Used for storage of working materials, temporary storage of tools, access to other areas.In the sketch I describe.
(not on scale).
Following NFPA 72, I interpret the upper level shall be considerd a different case.
The detector spacing looks fine for the high ceiling area, but in the upper level the size of beams lead me to a detector in each beam pocket.
A little beyond my little knowledge.
I do not think you can get a reduction for low ceiling, unless some engineering analysis is done?
Waiting for Scott to answer you.
From the 2013 edition, does this help you::
Looks like you fall between a solid joist and a beam.
If all else fails, can they sheetrock the area?? And make it smooth? would it be cheaper in the long run?
17.6.3.3* Beam Construction.
17.6.3.3.1 Spacing.
17.6.3.3.1.1 A ceiling shall be treated as a smooth ceiling if the beams project no more than 4 in. (100 mm) below the ceiling.
17.6.3.3.1.2 Where the beams project more than 4 in. (100 mm) below the ceiling, the spacing of spot-type heat detectors at right angles to the direction of beam travel shall be not more than two-thirds of the listed spacing.
17.6.3.3.1.3 Where the beams project more than 18 in. (460 mm) below the ceiling and are more than 8 ft (2.4 m) on center, each bay formed by the beams shall be treated as a separate area.
17.6.3.3.2 Location. Where beams are less than 12 in. (300 mm) in depth and less than 8 ft (2.4 m) on center, detectors shall be permitted to be installed on the bottom of beams.