SNORGY
Mechanical
- Sep 14, 2005
- 2,510
I am looking at a propane condenser (air cooler) with a relief valve discharging to a flare system. I interpret API-521 to suggest that, with free drainage to the accumulator, I do not need to size for fire based on bundle bare tube area; in fact, I don't need to put the relief valve in at all. However, the process packager has installed one and piped it to flare. The orifice size is "P". If one is to assume the full relief valve capacity in terms of mass flux rate at the flare tip, the GLR from the stack exceeds regulatory allowance by a factor of 3.0, and, correspondingly, the stack is 100 feet too short.
The condenser actual volume is about 4% of the flare system actual volume. Understanding that the propane at condenser pressure has a mass (vapor-based) approximately equal to the mass of air and purge gas in the flare system, and that the relieving event duration is less than 2 seconds, and that the stack is about 350 feet away, do I need to assume that full mass flux rate of pure propane exiting the flare tip, or is there some accepted way of quantifying the effects of mixing and displacement that might contribute towards the reduction of heating value and GLR? If such a calculation methodology exists, can someone point me towards it?
I have this picture in my mind of a valve going fully closed to fully open for 2 seconds at one end of 350 feet of 18"-D pipe and waiting for this instantaneous plume of gargantuan proportions frying everything within 100 yards of it...and I am struggling with accepting it.
The condenser actual volume is about 4% of the flare system actual volume. Understanding that the propane at condenser pressure has a mass (vapor-based) approximately equal to the mass of air and purge gas in the flare system, and that the relieving event duration is less than 2 seconds, and that the stack is about 350 feet away, do I need to assume that full mass flux rate of pure propane exiting the flare tip, or is there some accepted way of quantifying the effects of mixing and displacement that might contribute towards the reduction of heating value and GLR? If such a calculation methodology exists, can someone point me towards it?
I have this picture in my mind of a valve going fully closed to fully open for 2 seconds at one end of 350 feet of 18"-D pipe and waiting for this instantaneous plume of gargantuan proportions frying everything within 100 yards of it...and I am struggling with accepting it.