I am a civil engineer reviewing an assessment report concerning a multi-building facility.
They have a photo of the main switchboard with the label reading Main 3,000 amps, 3 pole, 120/208 volt.
The report then makes the following calculation, which I believe is wrong:
The calculation they have is 3000*3*120 to get 1,080 kVA.
It is my understanding that three phase power should be the square root of 3, so I would get:
3000*1.782*120 to get about 641 kVA.
These are commercial/residential buildings, so I am not concerned with power factor for this study phase of the project.
I would appreciate any corrections of my assumptions.