Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Shield Voltage Calculation for 25kV

Status
Not open for further replies.

cherry2000

Electrical
Jun 21, 2007
99
I wanted to know if anybody has carried out calculations for a. Floating voltage b. Circulating current & c.Shield loss per unit length...for 25kV, 3C, cable with core shields ungrounded at one end / grounded at both ends. Interestingly, some relevant sections in IEEE 525-2007 have been removed and there is not much to fall back on.
 
Replies continue below

Recommended for you

According to EPRI EL-5036 Power Plant Electrical Reference Series, Vol. 4, “Wire and Cable”
ch. Shield Impedances.
Xm=2*Pi()*F*(0.1404*LOG10(S/rm)) micro OHM/ft
Let's take a 25 kV 3*500 MCM copper conductor cable [Okonite]
S=1.48 in. rm=1.49/2 F=60 Irated=600 A [in air 40oC] 1000 ft length
Xm=16.09 /10^6 ohm/ft
Induced voltage= Irated*Xm=0.0096523 V/ft 9.65 volt/1000 ft
 
Thanks alehman & 7anoter4..I shall go through the literature and let you know what I get..Thanks again!
 