Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Shear strength of embedded anchor bolts in CMU

Status
Not open for further replies.

EBF

Structural
Jun 2, 2003
62
If I have anchor bolts embedded in a CMU wall (f'm=1500psi)that is fully grouted (grout f'c=4000psi), is it ok to use the shear strength values from 1997 UBC Table 19-D for bolts embedded in concrete, rather than the values listed in Table 21-E for bolts embedded in masonry? Or do the values for masonry already take into account fully grouted units with higher strength grout?
 
Replies continue below

Recommended for you

I think your problems can be best answered by a question also.

Who’s holding the grout?

I will use the values listed in bolts embedded in masonry, even if it is 1,000,000psi grout (just exaggerating).

For your second question, my answer is “ perhaps they already consider a certain strength of grout but maybe not higher “.

Many thanks.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor