So from what I've read, when you have a generator or other alternate power source, and transfer switch, each is a SDS, and that switch should switch the neutral as well. Neutral is grounded at the source.
But the case I'm looking at will have a utility xfmr w/wye secondary at the transfer switch, and an adjacent genset, and the inverters, all within a few feet. I would think all would share the same ground point -- the rod+Ufer etc. at that point. If so, is there still a requirement to switch the neutral?
But the case I'm looking at will have a utility xfmr w/wye secondary at the transfer switch, and an adjacent genset, and the inverters, all within a few feet. I would think all would share the same ground point -- the rod