Residual Current Devise (RCD)

Status
Not open for further replies.

salem

Electrical
May 2, 2001
38
0n 415 V TT earthed system, Can we use Residual Current Device (RCD) at load side.

I'm having a case where RCD is tripping when we supply from portable generator with unearthed neutral, but not tripping when we supply from a transformer with earthed neutral.
 
Replies continue below

Recommended for you

One of your loads may have a capacitive leak that results in an imbalance that would normally be split or resolved via the source's ground which is missing with your generator.

Keith Cress
kcress -
 
The first step will be to ground the generator neutral. If it still trips, check the waveform of the generator output with a scope.
Otherwise as itsmoked suggests or other load related issues.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Question is, do you want to run your system as IT or TT?
 