nilbhadane

Structural
Aug 28, 2012
1
Dear All,

As per ACI 318 cl. 21.3.2.2 "the positive moment strength at joint face shall be not less than one-half of the negative moment strength provided at that face of the joint. Neither the negative nor the positive moment strength at any section along member length shall be less than one-fourth the maximum moment strength provided at face of either joint."( ref ACI 318).
My query is whether this clause is applicable for cantilever type of pier cap/pier heads with single pier?

I think as there no possibility of reversal of forces even in case of seismic or any other load case, the minimum 12 mm dia bars are sufficient for these kind of structures.

regards,

NB
 
Replies continue below

Recommended for you

That provision applies only to special moment frames. It has moved to 21.5.2.2 in 318-11.

Within the constraints, I would expect a bent across a single pier would need to meet the requirements since it is part of the lateral system.
 