- 467
I am not a harmonics guru and so need some advice please in planning a network. A client wishes to use 6 pulse inverter VFD's on drives from 250kW to 500kW at 480V. Naturally there will be substantial 5th and 7th harmonics present. Currently, the 13.8kV/480V 1.5MVA transformers, supplying these drives, are delta-star. Star neutral grounded. The client has asked me to consider a Yyn0 and Dd0 trfr instead of the Dyn11 as a mitigation measure.
I am wondering how these will help though as the 5th and 7th are not triplen and therefore not zero sequence harmonics so I do not see much use in a trfr delta winding as a mitigation measure. Besides a Dd0 trfr also means the 480V network is not earthed and that's another problem.
Yyn0 means zero sequence currents from the LV cannot be reflected to the HV (HV neutral not grounded but LV is) as zps currents as there is no delta (3 core trfr) to provide the ampere-turns balance. I do know the tank delta effect comes into play - but that's besides the point as the 5th and 7th are not zps harmonics.
Was wondering if someone could confirm my understanding above or show me the grievious errors of my ways!
Thanks.
I am wondering how these will help though as the 5th and 7th are not triplen and therefore not zero sequence harmonics so I do not see much use in a trfr delta winding as a mitigation measure. Besides a Dd0 trfr also means the 480V network is not earthed and that's another problem.
Yyn0 means zero sequence currents from the LV cannot be reflected to the HV (HV neutral not grounded but LV is) as zps currents as there is no delta (3 core trfr) to provide the ampere-turns balance. I do know the tank delta effect comes into play - but that's besides the point as the 5th and 7th are not zps harmonics.
Was wondering if someone could confirm my understanding above or show me the grievious errors of my ways!
Thanks.