Hello folks.
I need some advice / opinion
We are are going to be supervising an construction of medium size residential building.
Dsigner has defined and raft foundation 20cm thick with and edge beam thats 30cm in width and 50 cm in total height.
The raft slab is reinfroced in top and bottom layer and the edge beam also.
I did a simple hand calculation on pressure contacts beneathe the edge beam thats 30cm wide.
A line load thats coming from the bearing wall, directly above the edge beam is around 100kN/m.
This is resulting with and contact pressure of an 333,33kN/m2 (100kN/m divided by width 0,30m)
I know this is pure simplification but allowable contact pressure is 200kN/m2.
Shouldnt the beam width be wider?!
I understand that this is an raft but there is going to be a lot od high pressure concentration under the edge beam, since the bearing wall is directly above it. Wont this result with an soil failure?
I need some advice / opinion
We are are going to be supervising an construction of medium size residential building.
Dsigner has defined and raft foundation 20cm thick with and edge beam thats 30cm in width and 50 cm in total height.
The raft slab is reinfroced in top and bottom layer and the edge beam also.
I did a simple hand calculation on pressure contacts beneathe the edge beam thats 30cm wide.
A line load thats coming from the bearing wall, directly above the edge beam is around 100kN/m.
This is resulting with and contact pressure of an 333,33kN/m2 (100kN/m divided by width 0,30m)
I know this is pure simplification but allowable contact pressure is 200kN/m2.
Shouldnt the beam width be wider?!
I understand that this is an raft but there is going to be a lot od high pressure concentration under the edge beam, since the bearing wall is directly above it. Wont this result with an soil failure?