rogerj1
Electrical
- Jan 5, 2007
- 23
We had a PVD High Impedance Bus Diff relay misop for an out of zone LG fault. Quite frankly, I'm not that knowledgeable about High Z style relaying schemes. This was installed years ago and we now use percentage current diff's on most all 87B schemes now. And of course its electromech and we have no other means of fault recording so there's no records to review. So far, we have verified the following:
1. All CTR's used for this relay are on the same ratio, 240:1
2. It was found there is no ground at all on the secondary current circuits . All CT's are wired in a WYE fashion, and they're all landed together in parallel for all phases/nuetrals wired into the relay.
It is my suspicion that the lack of a single ground point on the secondary circuits may have been the culprit. I've found the issue with grounding is more commonly the unexpected extra grounds to be a cause of trouble, but in this case we have no ground at all. Furthermore, I can't find any documented cases of trouble where the lack of a single common ground has caused trouble as well. Considering I'm not so familiar with the High Impedance 87B method makes it all the more confusing. I would appreciate your comments/suggestions on the topic here and anything else you could offer on the topic of missing grounds in a WYE connected secondary CT circuit.
Thanks
1. All CTR's used for this relay are on the same ratio, 240:1
2. It was found there is no ground at all on the secondary current circuits . All CT's are wired in a WYE fashion, and they're all landed together in parallel for all phases/nuetrals wired into the relay.
It is my suspicion that the lack of a single ground point on the secondary circuits may have been the culprit. I've found the issue with grounding is more commonly the unexpected extra grounds to be a cause of trouble, but in this case we have no ground at all. Furthermore, I can't find any documented cases of trouble where the lack of a single common ground has caused trouble as well. Considering I'm not so familiar with the High Impedance 87B method makes it all the more confusing. I would appreciate your comments/suggestions on the topic here and anything else you could offer on the topic of missing grounds in a WYE connected secondary CT circuit.
Thanks