SmilerFDL
Chemical
- Jul 10, 2014
- 5
Hi all,
I'm comparing different sources on various subjects of safety relief valves and found different diagrams showing a "typical" valve opening/closing characteristic.
Of course there is API520 (8th ed.) which provides figure 6 (page 14), the Consolidated Catalogue for Safety Relief Valves (dated Oct. 2008), the LESER handbook ( and SpiraxSarco ( describe PSV operation. Of course there are more sources.
The curve from API, is similar to the diagram in the Consolidated catalogue, where the PRV lifts to 50%-60% right at set pressure and then continously lifts with further pressure increase. Closing is proportional to the pressure decrease, API starts closing at ~105% of set pressure, Consolidated at 98% of set. Valve reseats at the required blowdown of 93% set pressure.
In contradiction the diagrams of LESER and SpiraxSarco show proportional opening to ~104% set pressure, then (nearly) full opening at ~105% set pressure. Closing starts at 99% of set pressure and is rather parabolic then proportional, also reseating within the blowdown limit.
I assume the latter show curves for pop-action ("safety") valves, while API and Consolidated show "relief" valves? Anyhow I wonder, why API and Consolidated instantly open at virtually set pressure, while others need huddling chamber etc. to overcome spring force.
Which leads me to another question bothering me: What range is the additional force required to compress the spring to 100% disc lift? I expect the force is linear with the lift and should not exceed 105% of CDTP? Or even less?
CU, Smiler
I'm comparing different sources on various subjects of safety relief valves and found different diagrams showing a "typical" valve opening/closing characteristic.
Of course there is API520 (8th ed.) which provides figure 6 (page 14), the Consolidated Catalogue for Safety Relief Valves (dated Oct. 2008), the LESER handbook ( and SpiraxSarco ( describe PSV operation. Of course there are more sources.
The curve from API, is similar to the diagram in the Consolidated catalogue, where the PRV lifts to 50%-60% right at set pressure and then continously lifts with further pressure increase. Closing is proportional to the pressure decrease, API starts closing at ~105% of set pressure, Consolidated at 98% of set. Valve reseats at the required blowdown of 93% set pressure.
In contradiction the diagrams of LESER and SpiraxSarco show proportional opening to ~104% set pressure, then (nearly) full opening at ~105% set pressure. Closing starts at 99% of set pressure and is rather parabolic then proportional, also reseating within the blowdown limit.
I assume the latter show curves for pop-action ("safety") valves, while API and Consolidated show "relief" valves? Anyhow I wonder, why API and Consolidated instantly open at virtually set pressure, while others need huddling chamber etc. to overcome spring force.
Which leads me to another question bothering me: What range is the additional force required to compress the spring to 100% disc lift? I expect the force is linear with the lift and should not exceed 105% of CDTP? Or even less?
CU, Smiler