Dear All,
I am talking about Double Wye ungrounded Capacitor Unbalance protection using Neutral CT and neutral VT as explained in IEEE C37.99-2000 section 8.2.6.2.
i have 13.8KV capacitor bank double way ungrounded and both unbalance protection approches are used:
CT approach: CT will be connected to 51N relay in order to detect any fuse blown. the problem of this apprach in that no current will flow in the neutral in case of identical fuse blown in both legs of the same phase.
VT apprach: VT wil be connected to 59N relay to detect any unbalance. this apprach overcomes the 51N limitation.
the prblem i am facing is that 59N relay operated many time for other 13.8KV feeders faults while the 51N is stable.
any explanation please?
thank you,