Power Transformers typical impedance values

Status
Not open for further replies.

tctctraining

Electrical
Nov 17, 2008
118
We are working on a project and need to define typical ( conservative ) impedance values for Delata-Wye and Wye-G, Wye-G, Delta transformers. Transformers are 18/25/30 Mva 230kV/34.5 kV. Where can I find these typical values?
I apprecite your responces.

 
Replies continue below

Recommended for you

Also, there are standard impedance values given in ANSI C57 - based on the high side BIL. If you don't have access to ANSI C57, any transformer manufacturer can give you the standard impedances.

 
To know generally specified impedance values for transformers around the world, refer to IEC TR60909-2 ed2.0(2008-11) Data for electrical equipment for short circuit current calculations.
 