Prologue
Our facility uses a 10 MVA, 69kV:12470V transformer to feed a mixture of 12470:480 transformers (mostly delta-wye, but with one 3750 KVA delta-delta, and a 2500 KVA wye-wye). The utility doesn't charge for low power factor, but we're planning several process line additions, and must either significantly improve power factor (nominally 78 to 80%) to free up capacity, or do extensive work to increase KVA.
One complicating factor is, while we have a number of high power across-the-line, and delta-wye started motors a significant portion of our load are DC motors ranging from 250 HP to 700 HP driven from S-6 bridges. Newer machines - about 1200 HP worth per nameplate - are using AC motors driven with ABB ACS800 drives, but, so far, none were built using the -ULH ultra low harmonic option. Our newer AC and DC drive installations are equipped with 3% line reactors or isolation transformers, but those on older installations are connected directly to the bus.
One proposed solution is to install controlled capacitor banks in the 12470 transformer yards to operate at nearly unity. While this would free up KVA and eliminate the need to re-work the 10 MVA transformer and lines to it I'm feeling incredibly queasy at the prospect of potential harmonics and resonance issues.
I'm thinking a better scheme is to install properly sized capacitor banks at larger (30 HP and up) across-the-line and delta-wye started motors, install line reactors on DC drives that aren't already so equipped (eventually we'll be phasing these out in favor of AC drives), and to specify ABB ACS800 drives with the -ULH option for new installations.
I've read previous Eng-Tips threads, but haven't yet run across one on this specific question ...
In several cases - process pumps, cooling tower fans, and air compressors (where we use a single VSD compressor for trim control, and our sequenced fixed capacity compressor motors run fully loaded most of the time)KVAR sizing isn't very difficult.
However, each of our process lines use a 75 HP or 100 HP reclaim granulator, and on these the load profile changes dramatically. During normal process operations they run lightly loaded, but must be sized to allow for periods of heavy scrap generation.
It seems to me using a controlled PFC bank for these would be problematic (in addition to costly) due to the very 'peaky' load profile. If I size to correct PF at nominal loading then it'll over-correct under heavier loads.
I'm leaning towards KVAR sizing to achieve 95% PF from whatever the power factor is at peak recorded loads (in this case, from 85% to 95%), and am interested in any opinions pro or con, and/or if there are rules-of-thumb when sizing KVAR caps for highly variable loads.
Trending for a typical installation is attached.
Our facility uses a 10 MVA, 69kV:12470V transformer to feed a mixture of 12470:480 transformers (mostly delta-wye, but with one 3750 KVA delta-delta, and a 2500 KVA wye-wye). The utility doesn't charge for low power factor, but we're planning several process line additions, and must either significantly improve power factor (nominally 78 to 80%) to free up capacity, or do extensive work to increase KVA.
One complicating factor is, while we have a number of high power across-the-line, and delta-wye started motors a significant portion of our load are DC motors ranging from 250 HP to 700 HP driven from S-6 bridges. Newer machines - about 1200 HP worth per nameplate - are using AC motors driven with ABB ACS800 drives, but, so far, none were built using the -ULH ultra low harmonic option. Our newer AC and DC drive installations are equipped with 3% line reactors or isolation transformers, but those on older installations are connected directly to the bus.
One proposed solution is to install controlled capacitor banks in the 12470 transformer yards to operate at nearly unity. While this would free up KVA and eliminate the need to re-work the 10 MVA transformer and lines to it I'm feeling incredibly queasy at the prospect of potential harmonics and resonance issues.
I'm thinking a better scheme is to install properly sized capacitor banks at larger (30 HP and up) across-the-line and delta-wye started motors, install line reactors on DC drives that aren't already so equipped (eventually we'll be phasing these out in favor of AC drives), and to specify ABB ACS800 drives with the -ULH option for new installations.
I've read previous Eng-Tips threads, but haven't yet run across one on this specific question ...
In several cases - process pumps, cooling tower fans, and air compressors (where we use a single VSD compressor for trim control, and our sequenced fixed capacity compressor motors run fully loaded most of the time)KVAR sizing isn't very difficult.
However, each of our process lines use a 75 HP or 100 HP reclaim granulator, and on these the load profile changes dramatically. During normal process operations they run lightly loaded, but must be sized to allow for periods of heavy scrap generation.
It seems to me using a controlled PFC bank for these would be problematic (in addition to costly) due to the very 'peaky' load profile. If I size to correct PF at nominal loading then it'll over-correct under heavier loads.
I'm leaning towards KVAR sizing to achieve 95% PF from whatever the power factor is at peak recorded loads (in this case, from 85% to 95%), and am interested in any opinions pro or con, and/or if there are rules-of-thumb when sizing KVAR caps for highly variable loads.
Trending for a typical installation is attached.