It recently came to my attention that several operating companies are opening parallel, 100% sized, relief valves to the process when the design was to leave one closed and one open to facillitate maintenance. This is apparently becoming a standard practice.
If more than one relief device is applied to a process and operated in parallel, the set points are staggered by 5% and designed to not allow an overpressure greater than 16%. These devices are sized such that the combined capacity does not exceed around 140% of the required capacity.
When parallel relief valves are installed and each is sized for 100+% of required capacity, the intent is to provide a spare that is closed to the process; this facillitates maintenance and testing. It is very bad practice, even dangerous practice, to open both of these valves to the process. In all fairness, this is done because it is perceived to be safer. In reality, it is not.
Without going into detail here, flare loading and pipe stress calculations are made based on P&ID's and the philosophy at the time of design. To open both valves to the process when this was not intended can result in a number of unwanted consequences to included:
- Transient Flare System overload - Capacity and Pressure
- Pipe Support Damage
- Relief pipe damage
- Damage to relief valves
- Less than required relief capacity
- Liability: Plant Operating not in accordance with approved P&ID's
I have looked at this in detail and have more information on the subject.
If more than one relief device is applied to a process and operated in parallel, the set points are staggered by 5% and designed to not allow an overpressure greater than 16%. These devices are sized such that the combined capacity does not exceed around 140% of the required capacity.
When parallel relief valves are installed and each is sized for 100+% of required capacity, the intent is to provide a spare that is closed to the process; this facillitates maintenance and testing. It is very bad practice, even dangerous practice, to open both of these valves to the process. In all fairness, this is done because it is perceived to be safer. In reality, it is not.
Without going into detail here, flare loading and pipe stress calculations are made based on P&ID's and the philosophy at the time of design. To open both valves to the process when this was not intended can result in a number of unwanted consequences to included:
- Transient Flare System overload - Capacity and Pressure
- Pipe Support Damage
- Relief pipe damage
- Damage to relief valves
- Less than required relief capacity
- Liability: Plant Operating not in accordance with approved P&ID's
I have looked at this in detail and have more information on the subject.