Hello everyone,
I have run into a couple issues while trying to size a PSV in FluidFlow. The data for my problem and my questions are given below:
Data:
- FluidFlow sizing of PSV
- Working fluid is steam
- Design pressure of pipe is 1379 kPag
- PSV is protecting this pipe
- PSV design flow is 55167 kg/h
- Relief to atmosphere
Questions:
1. In order to avoid choked flow and sonic fluid velocity, we had to calculate using non-standard outlet piping sizes. The largest diameter standard size we used was 12 in Schedule 40S, but still resulted in sonic velocity. Using outlet piping that was 18 in Schedule 10 reduced our fluid velocity to below sonic, but it still remained high (274 m/s) and decreased with increasing pipe diameter, as expected. How should we tackle this problem to avoid using non-standard piping but simultaneously keep our fluid below sonic velocities?
2. Using the same parameters for question 1, our PSV area was calculated to be a non-standard size of 9801.6 mm2. The closest actual standard PSV area size is 11471 mm2 (Farris Engg PRVs). I am worried that the manufacturer’s size is too big, resulting in issues with our system. How can I check if the manufacturer’s size will still work for my system? I am unable to enter area values for my PSV in FluidFlow.
Thank you all for your help.
I have run into a couple issues while trying to size a PSV in FluidFlow. The data for my problem and my questions are given below:
Data:
- FluidFlow sizing of PSV
- Working fluid is steam
- Design pressure of pipe is 1379 kPag
- PSV is protecting this pipe
- PSV design flow is 55167 kg/h
- Relief to atmosphere
Questions:
1. In order to avoid choked flow and sonic fluid velocity, we had to calculate using non-standard outlet piping sizes. The largest diameter standard size we used was 12 in Schedule 40S, but still resulted in sonic velocity. Using outlet piping that was 18 in Schedule 10 reduced our fluid velocity to below sonic, but it still remained high (274 m/s) and decreased with increasing pipe diameter, as expected. How should we tackle this problem to avoid using non-standard piping but simultaneously keep our fluid below sonic velocities?
2. Using the same parameters for question 1, our PSV area was calculated to be a non-standard size of 9801.6 mm2. The closest actual standard PSV area size is 11471 mm2 (Farris Engg PRVs). I am worried that the manufacturer’s size is too big, resulting in issues with our system. How can I check if the manufacturer’s size will still work for my system? I am unable to enter area values for my PSV in FluidFlow.
Thank you all for your help.