magoo2
Electrical
- May 17, 2006
- 857
We have a single phase circuit 7200 V to ground in a beach area. The circuit runs 2 or 3 miles and the peak load is around 100 A on the phase. The neutral is multi-grounded.
In looking at the phase amps versus the neutral amps at different points along the circuit, I'm finding we're only getting about 1/3 of the current returning thru the neutral wire. I would have expected more like 1/2 to 1/1 split.
Any ideas?
In looking at the phase amps versus the neutral amps at different points along the circuit, I'm finding we're only getting about 1/3 of the current returning thru the neutral wire. I would have expected more like 1/2 to 1/1 split.
Any ideas?