Cap07
Structural
- Mar 8, 2008
- 78
Hi,
I need some help with a design for a sign. It is a 4’x8’ sign, supported by pressure treated wood posts. Please see the attached sketch. The jurisdiction requires that the sign and supporting structure be designed for a wind load of 30 psf. If I use tributary widths, I calculate a load on the center post of 480 lb:
Post load = (2’ + 2’)(4’)(30 psf) = 480 lb
The bottom edge of the sign is 3’ off of the ground, so I am calculating a moment of 2400 ft-lb at the post base:
Mpost = (3’ + 2’)(480) = 2400 ft-lb
I calculate that I need a 6x6 posts.
The thing that I am not sure about is the post embedment. I am calculating this using 2006 IBC section 1805.7. Specifically I am using the nonconstrained equation in section 1805.7.2.1:
d = 0.5A{1 + [1 + (4.36h/A)]½} Eq. 18-1
I don’t have any soil properties, so I am assuming the worst and using 100 psf for my lateral bearing value (per IBC Table 1804.2). If I use a 1.5 ft diameter concrete footing for the post, I calculate a embedment depth of almost 6.5 ft. Please see the attached spreadsheet. The calculation is an iterative process, so I assumed an initial depth, then continued until the assumed depth equaled the calculated depth.
My question is - does my calculational approach seem reasonable and does the depth I’m coming up with sound reasonable? It seems awfully deep to me.
Thanks in advance for any help or advice you can provide. It is most appreciated!
Cap
I need some help with a design for a sign. It is a 4’x8’ sign, supported by pressure treated wood posts. Please see the attached sketch. The jurisdiction requires that the sign and supporting structure be designed for a wind load of 30 psf. If I use tributary widths, I calculate a load on the center post of 480 lb:
Post load = (2’ + 2’)(4’)(30 psf) = 480 lb
The bottom edge of the sign is 3’ off of the ground, so I am calculating a moment of 2400 ft-lb at the post base:
Mpost = (3’ + 2’)(480) = 2400 ft-lb
I calculate that I need a 6x6 posts.
The thing that I am not sure about is the post embedment. I am calculating this using 2006 IBC section 1805.7. Specifically I am using the nonconstrained equation in section 1805.7.2.1:
d = 0.5A{1 + [1 + (4.36h/A)]½} Eq. 18-1
I don’t have any soil properties, so I am assuming the worst and using 100 psf for my lateral bearing value (per IBC Table 1804.2). If I use a 1.5 ft diameter concrete footing for the post, I calculate a embedment depth of almost 6.5 ft. Please see the attached spreadsheet. The calculation is an iterative process, so I assumed an initial depth, then continued until the assumed depth equaled the calculated depth.
My question is - does my calculational approach seem reasonable and does the depth I’m coming up with sound reasonable? It seems awfully deep to me.
Thanks in advance for any help or advice you can provide. It is most appreciated!
Cap