Dear colleagues,
It is interesting to hear some opinions on the issue that seems to be confusing. Below is a quotation from NEC (2014 Edition):
430.122 Conductors — Minimum Size and Ampacity.
(A) Branch/Feeder Circuit Conductors. Circuit conductors
supplying power conversion equipment included as
part of an adjustable-speed drive system shall have an ampacity
not less than 125 percent of the rated input current to
the power conversion equipment.
Consider Adjustable Speed Drive (ASD) system that always includes stand alone Drive Isolation Transformer (DIT)in the scope of supply of the ASD system. We generally state that the DIT primary terminals is a "border" of the ASD system, customer has to provide adequately sized and protected feeder from the grid to DIT primary. I see the following interpretations of how to apply the above article:
1. 125% factor applies ONLY to the conductors from the grid to DIT primary (power conversion equipment is defined as inclusive the DIT)
2. 125% factor applies ONLY to conductors from the DIT secondary winding terminals to the drive cabinets (power conversion equipment includes the drive cabinet(s) itself.
3. 125% factor applies to BOTH conductor runs (grid - primary and secondary - drive cabinet)
What variant would you consider correct? This issue has significant economical implications for large ASD systems.
It is interesting to hear some opinions on the issue that seems to be confusing. Below is a quotation from NEC (2014 Edition):
430.122 Conductors — Minimum Size and Ampacity.
(A) Branch/Feeder Circuit Conductors. Circuit conductors
supplying power conversion equipment included as
part of an adjustable-speed drive system shall have an ampacity
not less than 125 percent of the rated input current to
the power conversion equipment.
Consider Adjustable Speed Drive (ASD) system that always includes stand alone Drive Isolation Transformer (DIT)in the scope of supply of the ASD system. We generally state that the DIT primary terminals is a "border" of the ASD system, customer has to provide adequately sized and protected feeder from the grid to DIT primary. I see the following interpretations of how to apply the above article:
1. 125% factor applies ONLY to the conductors from the grid to DIT primary (power conversion equipment is defined as inclusive the DIT)
2. 125% factor applies ONLY to conductors from the DIT secondary winding terminals to the drive cabinets (power conversion equipment includes the drive cabinet(s) itself.
3. 125% factor applies to BOTH conductor runs (grid - primary and secondary - drive cabinet)
What variant would you consider correct? This issue has significant economical implications for large ASD systems.