Has anybody here used Medium voltage EMI filter to mitigate 4160V VFD telephone interence?

I am looking for the real product to deal with this issue?
Thanks in advance.
 
Replies continue below

Recommended for you

MTE doesn't make any Medium Voltage EMI Filter.
 
have you tried working with your MV VFD vendor? I am assuming you have one sense it appears this is the source of your issue.

in general, I would recommend getting an accurate model of your system including modeling your harmonic injections from VFDs and then determine what you want to use to mitigate your problem. For instance a properly sized and placed reactor used as a choke would be a possible solution. there are many manufactures of MV reactors although they probably aren't advertised as EMI mitigation.
 