Folks,
thread238-447179 posted 10 Dec 2018 asked about relay behaviour when protection CTs were double earthed. Some testing at site has confirmed that there is a single earth reference for the CT secondary circuit. The CT earht5ing was not, therefore, responsible for the nuisance earth fault trip.
Since that post I have noticed that there is a 130 metre run of cable ladder carrying the pair of cable circuits, one of which, clr1-AA3,tripped when it erroneously measured an earth fault current of 60 A.
Please see Fig.1 which is the single line of the system in question marked with some flux linkage which is the subject of this query. The cables are 19/33 kV, 400 mm² 1c., Cu, XLPE, AWA and are arranged in trefoil.
Fig.2 shows the cable layout on the 600 mm wide cable ladder.
Fig.3 is the zero phase sequence network, as I see it. My questions are:
1. "How can I determine the flux from one circuit cutting each core of the opposite circuit?
2. Has anyone experienced similar earth fault operations in a tie circuit between two sections of a power station or substation busbar where there are several solidly earthed star windings on either side of the tie circuit?"
thread238-447179 posted 10 Dec 2018 asked about relay behaviour when protection CTs were double earthed. Some testing at site has confirmed that there is a single earth reference for the CT secondary circuit. The CT earht5ing was not, therefore, responsible for the nuisance earth fault trip.
Since that post I have noticed that there is a 130 metre run of cable ladder carrying the pair of cable circuits, one of which, clr1-AA3,tripped when it erroneously measured an earth fault current of 60 A.
Please see Fig.1 which is the single line of the system in question marked with some flux linkage which is the subject of this query. The cables are 19/33 kV, 400 mm² 1c., Cu, XLPE, AWA and are arranged in trefoil.
Fig.2 shows the cable layout on the 600 mm wide cable ladder.
Fig.3 is the zero phase sequence network, as I see it. My questions are:
1. "How can I determine the flux from one circuit cutting each core of the opposite circuit?
2. Has anyone experienced similar earth fault operations in a tie circuit between two sections of a power station or substation busbar where there are several solidly earthed star windings on either side of the tie circuit?"