sykimk
Electrical
- Dec 28, 2003
- 55
We have total six (6) GTGs (all 15 MVA, 11kV generators) and all generators will be connected to a common 11kV bus. i.e. all generators in parallel and individually grounded. We have initially selected 100A NGR for each generator without neutral switching device.
In addition, we also have two 11kV/6.6kV distribution transformers with a vector group of YNyn0+D11. Common 11kV generator bus will also feed these transformers. HV side of these transformers is also grounded with 100A NGR (No neutral switching device). FYI, these transformers are used for feeding our Essential 6.6kV bus and all other distribution transformers have a vector group of Dyn11.
I understood that many references recommend neutral switching device for individually grounded generators and only one generator grounded in the system. But my client does not want to have neutral switching device since there is possibility of ungrounded system operation. It is their biggest concerns and there is no way to change my client’s mind.
Now we had 3rd harmonic circulating current concerns and generator manufacturer recommended 40A NGR for generator neutral grounding to reduce 3rd harmonic circulating current not to damage generators.
But we have lots of 11kV distribution cable feeders in the system, and capacitance charging current of cables (all feeders) will be about 30.1A. For the worst case consideration, I assumed only one generator running and all feeders are closed for ready to energize secondary substations. In this case, the maximum charging current will be about 33.4A. Therefore, I think 40A NGR would be OK.
Now, we are about to make final decision to select 40A NGR (NO neutral switching device) for generator neutral grounding (i.e. individually grounded).
If we have GTG load sharing modules to control active & reactive power and put generators in voltage control mode, does it help us to reduce 3rd harmonic circulating current? As far as I know, generator 3rd harmonic voltage is dependent upon generator loading. If all generators have been equally loaded, I assume there will be no 3rd harmonic circulating current between generators but circulating current will flow between generator and NGR (100A) of transformer primary winding. Therefore, I also need to change transformer primary NGR size from 100A to 40A as well in order to keep low 3rd harmonic circulating current.
Did I understand correctly??
If I remove NGR from transformer primary winding (YNyn0+D11), i.e. ungrounded primary side, are there any adverse outcomes? I assume it would be the best for my case. i.e., individually grounded (40A each) generators in parallel and no additional grounding on the primary winding of YNyn0+D11 transformers (floated wye).
Could you please advise if I missed some points in this situation? Do you have any further recommendations for my case?
Thanks in advance for your advices and recommendations.
In addition, we also have two 11kV/6.6kV distribution transformers with a vector group of YNyn0+D11. Common 11kV generator bus will also feed these transformers. HV side of these transformers is also grounded with 100A NGR (No neutral switching device). FYI, these transformers are used for feeding our Essential 6.6kV bus and all other distribution transformers have a vector group of Dyn11.
I understood that many references recommend neutral switching device for individually grounded generators and only one generator grounded in the system. But my client does not want to have neutral switching device since there is possibility of ungrounded system operation. It is their biggest concerns and there is no way to change my client’s mind.
Now we had 3rd harmonic circulating current concerns and generator manufacturer recommended 40A NGR for generator neutral grounding to reduce 3rd harmonic circulating current not to damage generators.
But we have lots of 11kV distribution cable feeders in the system, and capacitance charging current of cables (all feeders) will be about 30.1A. For the worst case consideration, I assumed only one generator running and all feeders are closed for ready to energize secondary substations. In this case, the maximum charging current will be about 33.4A. Therefore, I think 40A NGR would be OK.
Now, we are about to make final decision to select 40A NGR (NO neutral switching device) for generator neutral grounding (i.e. individually grounded).
If we have GTG load sharing modules to control active & reactive power and put generators in voltage control mode, does it help us to reduce 3rd harmonic circulating current? As far as I know, generator 3rd harmonic voltage is dependent upon generator loading. If all generators have been equally loaded, I assume there will be no 3rd harmonic circulating current between generators but circulating current will flow between generator and NGR (100A) of transformer primary winding. Therefore, I also need to change transformer primary NGR size from 100A to 40A as well in order to keep low 3rd harmonic circulating current.
Did I understand correctly??
If I remove NGR from transformer primary winding (YNyn0+D11), i.e. ungrounded primary side, are there any adverse outcomes? I assume it would be the best for my case. i.e., individually grounded (40A each) generators in parallel and no additional grounding on the primary winding of YNyn0+D11 transformers (floated wye).
Could you please advise if I missed some points in this situation? Do you have any further recommendations for my case?
Thanks in advance for your advices and recommendations.