Two picking points will be used to lift a precast column during construction. At each lifting eye, the baseplate is fastened to the column with four 1-1/4" A325 bolts. These bolts will be attached to a coupler and 1-1/4" B5S "stress gradient" pigtail embedded in the concrete. The connection will be slip critical, so the bolts are required to be pretensioned to at least 71 k, which is 70% of the tensile strength of the bolt. The pigtail has an ultimate strength of 102 k, and the Williams catalog lists a Safe Working Load of 51 k (F.S.=2).
My questions are:
If the 1-1/4" A325 bolts are pretensioned to the recommended 71 k, how much of this force is transferred to the pigtails? Will the safety factor be 102/71 = 1.44, or is that conservative?
During lifting, the clamping force will be reduced by the axial tension in the bolt, but there will be sufficient clamping force to resist shear. If the pretension could be reduced to say 50 k, the pigtails would not be exceeding the manufacturer recommended safe working load of 51 k. However, 50 k is only about 50% of the tensile strength. Why is 70% specified by AISC/ASTM as the minimum bolt pretension?
Thanks!
My questions are:
If the 1-1/4" A325 bolts are pretensioned to the recommended 71 k, how much of this force is transferred to the pigtails? Will the safety factor be 102/71 = 1.44, or is that conservative?
During lifting, the clamping force will be reduced by the axial tension in the bolt, but there will be sufficient clamping force to resist shear. If the pretension could be reduced to say 50 k, the pigtails would not be exceeding the manufacturer recommended safe working load of 51 k. However, 50 k is only about 50% of the tensile strength. Why is 70% specified by AISC/ASTM as the minimum bolt pretension?
Thanks!