We are doing the commissioning of a direct online starter (DOL) 4.16kV, 778HP, 60Hz. medium voltage motor being used for a reaction furnace air blower. The airflow is controlled by a sensor which is upstream of the blower. The motor is tripping recently due to overload. Motor FLA=93.9A, LRA=564A at rated 4kV voltage and 0.18pf, motor rotor Wk2=40, full load torque (ft-lb)=1548, pull-up torque=60%, breakdown torque=280%, starting time at 100% rated voltage=14sec, and 25sec for 80% RV.
Multilin 369 relay device 49 overload pick-up set at 1.05xFLA, starting current is FLA x 6.7pu and apply the default overload standard curve multiplier value of 8. Acceleration time from start set at 16sec at 100% rated voltage. Device 27 starting U/V set at 0.8xrated, running U/V at 0.85xrated.
Immediately after the motor tripped, I retrieved data from the Multilin 369 motor protection relay and reveals that the motor tripped at the starting current=6.12xFLA, acceleration time=11.9sec, average motor load=394kW, phase current: A=546A, B=547A, C=550A, voltage: Vab=3.98kV, Vbc=3.99kV, Vca=4.08kV, frequency=59.96Hz, power factor=0.22lagging.
What exactly the cause of the overload trip after 11.9sec motor acceleration time. Do I need to account the other motor performance data for the custom overload curve? instead of relying on the default standard overload curve of the 369 MFR. Any ideas on why the motor is tripping on the above values.
Regards,
Bilegan
Murphy's Law - If anything can go wrong..it will.
Multilin 369 relay device 49 overload pick-up set at 1.05xFLA, starting current is FLA x 6.7pu and apply the default overload standard curve multiplier value of 8. Acceleration time from start set at 16sec at 100% rated voltage. Device 27 starting U/V set at 0.8xrated, running U/V at 0.85xrated.
Immediately after the motor tripped, I retrieved data from the Multilin 369 motor protection relay and reveals that the motor tripped at the starting current=6.12xFLA, acceleration time=11.9sec, average motor load=394kW, phase current: A=546A, B=547A, C=550A, voltage: Vab=3.98kV, Vbc=3.99kV, Vca=4.08kV, frequency=59.96Hz, power factor=0.22lagging.
What exactly the cause of the overload trip after 11.9sec motor acceleration time. Do I need to account the other motor performance data for the custom overload curve? instead of relying on the default standard overload curve of the 369 MFR. Any ideas on why the motor is tripping on the above values.
Regards,
Bilegan
Murphy's Law - If anything can go wrong..it will.